JDBrown
Senior Member
- Location
- California
- Occupation
- Electrical Engineer
If you have a balanced 3-phase MWBC, do you calculate the voltage drop the same way you would a 3-phase circuit with no neutral? My initial reaction was that of course you would calculate them the same way, but the more I think about it, the more I doubt that reaction.
When calculating single-phase voltage drop, I use:
VD = 2IR
For 3-phase I use:
VD = IR*sqrt(3)
where R is the one-way resistance of a conductor.
However, the more I think about it, the more I think I could get away with using VD = IR for a balanced MWBC.
Consider the following contrived example: Let's say there are 3 identical light fixtures installed so that each one is 10' away from a common junction box. A 100' homerun goes from the panel to the junction box, and from there it branches off to the 3 fixtures, with one fixture connected to each phase.

I would clearly use VD = 2IR to calculate the voltage drop from each fixture to the common junction box. I understand that the 2 in this formula comes from the fact that the current must travel up the phase conductor and back down the neutral conductor. However, in the case of the homerun, my neutral now carries the vector sum of all three phase currents. Since they are equal in magnitude, the total current on the neutral conductor is zero. Since the current on the homerun neutral is zero, the voltage drop is also zero. Therefore, it seems that the voltage drop on my homerun could be calculated as VD = IR.
Is this correct, or am I missing something? I expected to find a reason that I would need to include that sqrt(3) in the formula, as is required for a straight 3-phase circuit, but I'm not seeing it. Am I missing something here, or is the voltage drop really less for a balanced MWBC than for an equivalently sized 3-phase circuit?
When calculating single-phase voltage drop, I use:
VD = 2IR
For 3-phase I use:
VD = IR*sqrt(3)
where R is the one-way resistance of a conductor.
However, the more I think about it, the more I think I could get away with using VD = IR for a balanced MWBC.
Consider the following contrived example: Let's say there are 3 identical light fixtures installed so that each one is 10' away from a common junction box. A 100' homerun goes from the panel to the junction box, and from there it branches off to the 3 fixtures, with one fixture connected to each phase.

I would clearly use VD = 2IR to calculate the voltage drop from each fixture to the common junction box. I understand that the 2 in this formula comes from the fact that the current must travel up the phase conductor and back down the neutral conductor. However, in the case of the homerun, my neutral now carries the vector sum of all three phase currents. Since they are equal in magnitude, the total current on the neutral conductor is zero. Since the current on the homerun neutral is zero, the voltage drop is also zero. Therefore, it seems that the voltage drop on my homerun could be calculated as VD = IR.
Is this correct, or am I missing something? I expected to find a reason that I would need to include that sqrt(3) in the formula, as is required for a straight 3-phase circuit, but I'm not seeing it. Am I missing something here, or is the voltage drop really less for a balanced MWBC than for an equivalently sized 3-phase circuit?