Hello all! New to the board as I'm in need of some electrical advice.
A little background, I'm in the process of moving into a new building that has 3 phase electricity. Confirmed today that is 'high leg'. My main question is: I have been shopping around to PDU's to hook-up some computer equipment to and want to be sure it is compatible with the electricity service in my building! So confusing!!!
Here are the specs on two PDU's I'm looking at:
#1
Input Circuit: 200-208V 30A 3 phase Delta
Load Capacity: 8646VA @ 208V 3 phase
Input Connection: NEMA L15-30P
Questions about PDU #1... Will this PDU be compatible? With the NEMA L15-30P there are 4 prongs on the plug. X/BLACK (phase a?) + Y/RED (phase b - high leg?) + Z/ORANGE (phase c?) + G/GREEN (ground?). Are my notes here correct?
#2
Input Circuit: 208V 60A 3 phase Delta
Load Capacity: 17.3kVA @ 208V 3 phase
Input Connection: IEC309 3 Pole, 4 wire, 250VAC, 60A
Questions about PDU #2... same as above.
Any info would be greatly appreciated!
A little background, I'm in the process of moving into a new building that has 3 phase electricity. Confirmed today that is 'high leg'. My main question is: I have been shopping around to PDU's to hook-up some computer equipment to and want to be sure it is compatible with the electricity service in my building! So confusing!!!
Here are the specs on two PDU's I'm looking at:
#1
Input Circuit: 200-208V 30A 3 phase Delta
Load Capacity: 8646VA @ 208V 3 phase
Input Connection: NEMA L15-30P
Questions about PDU #1... Will this PDU be compatible? With the NEMA L15-30P there are 4 prongs on the plug. X/BLACK (phase a?) + Y/RED (phase b - high leg?) + Z/ORANGE (phase c?) + G/GREEN (ground?). Are my notes here correct?
#2
Input Circuit: 208V 60A 3 phase Delta
Load Capacity: 17.3kVA @ 208V 3 phase
Input Connection: IEC309 3 Pole, 4 wire, 250VAC, 60A
Questions about PDU #2... same as above.
Any info would be greatly appreciated!