Question?
Typically when I look at phase imbalance, I am measure phase to phase. I have a customer who is complaining that the voltage from phase to ground are imbalanced. The voltage between L1-L2 is 483, the voltage between L1-L3 IS 481, and the reading between L2-L3 is 486. So the phase are within < 1%. Good there. The Phase to ground readings are L1-G 279, L2-G 297, and L3-G is 280. The L2-G stands out. The equipment only has one 1 KVA single phase transformer. Since I never considered Phase to ground for determining balanced power, this is a strange worry by the customer. Any thoughts?
Typically when I look at phase imbalance, I am measure phase to phase. I have a customer who is complaining that the voltage from phase to ground are imbalanced. The voltage between L1-L2 is 483, the voltage between L1-L3 IS 481, and the reading between L2-L3 is 486. So the phase are within < 1%. Good there. The Phase to ground readings are L1-G 279, L2-G 297, and L3-G is 280. The L2-G stands out. The equipment only has one 1 KVA single phase transformer. Since I never considered Phase to ground for determining balanced power, this is a strange worry by the customer. Any thoughts?