what is the code section that say's phases can be in different pipes if they are bundled together. All the A phases in one pipe all the B phases in one pipe and all the C phases in another pipe. I was told it is in the new code....
It is a restrictive type of installation, because when installed incorrectly, it goes bad in a bad way.
Also, be aware that many utility companies do not like to approve this type of installation anymore, even if the NEC does. Make sure to talk to them and get it in writing.
If done correctly, using the code exceptions, each conduit will become a great on site cooking facility, just bring ferrous pots and sit them close to the raceway. Inductive cooking is the big rage in high end kitchens, and you'll have one for free.
I would have to agree with this 100%.
i'll see your 100% and raise you another 100%.
why would you want to do such a thing? what benefit is there?
I believe you could install the feeders in the way described as long as they were pulled into PVC conduit. You would also need enter the switchgear from the bottom like a duct bank so that there would not be any metal encircling the PVC conduits. Samething applies to the other end of the conduit run...no metal encircling the conduits. No metal bushings either(although I don't why anyone would put a metal bushing on the end of a PVC conduit unless they were worried about damaging the conduit during the installation of the feeder conductors.)
i'll see your 100% and raise you another 100%.
why would you want to do such a thing? what benefit is there?
Is that non-ferrous conduit?
Is that non-ferrous conduit?
So is this ok because the conduits are so close the wires are still able to cancel out each others magnetic field?