Jim in Ashland
New member
- Location
- United States
I am including a 300kW generator to handle a fraction of the loads for a new building. Approximately 2/3 of that generator will be on an ATS for non-emergency loads. The rest will be on an ATS dedicated for emergency lighting. The service is 1500kVA 480V grounded wye. I understand that places me in the position for providing ground fault protection at the service entrance - and I have done so. I seem to be chasing my tail to find the answer to whether or not the ATS' should be a 3 pole or a 4 pole devices. It is obvious that if the generator replaced the entire service then 4 pole devices are required. But in this instance we are a layer removed from the Service Entrance equipment and thus the breakers requiring ground fault protection it seems a 3 pole ATS is suitable. It then follows that the generator is NOT a separately derived system, and therefor can be grounded accordingly.