mshields
Senior Member
- Location
- Boston, MA
I have long been in the habit of specing 4 pole ATS's and treating the generator as a SDS; requiring that the contractor bond neutral to ground at the generator.
On a relatively small system I'm doing for a small 6 unit apt building, we're putting in a 208Y/120V generator for standby loads (they will still have EBU's for emergency lighting).
I speced, as is my habit a 4 pole ATS and showed a neutral to ground bond at the generator. I know this is fine, but I also know that 4 pole ATS's are more expensive.
Is there any reason not to go with a 3 pole ATS (so long as we don't bond N to G at the generator? The load is a mix of 3 phase motors and single phase lighting loads.
Thanks,
Mike
On a relatively small system I'm doing for a small 6 unit apt building, we're putting in a 208Y/120V generator for standby loads (they will still have EBU's for emergency lighting).
I speced, as is my habit a 4 pole ATS and showed a neutral to ground bond at the generator. I know this is fine, but I also know that 4 pole ATS's are more expensive.
Is there any reason not to go with a 3 pole ATS (so long as we don't bond N to G at the generator? The load is a mix of 3 phase motors and single phase lighting loads.
Thanks,
Mike