3 POLE VS 4 POLE DISCONNECT

Status
Not open for further replies.

kdce

New member
wE ARE ADDING AN AC DRIVE OFF 460 VAC 3 PHASE POWER AND THE DESIGNER IS ASKING ABOUT USING A 3 POLE OR 4 POLE FUSED DISCONNECT. WOULD WE ONLY NEED A 4 POLE IF WE ARE RUNNING RIGHT OFF INCOMING PLANT POWER THAT HAS NO TRANSFORMER BETWEEN THE POWER AND DRIVE? WHAT WOULD BE TH EREASON FOR A 4 POLE DISC?
THANKS.
 
Re: 3 POLE VS 4 POLE DISCONNECT

None.
No reason for a fourth pole, unless they wanted to open a grounded conductor.
 
Re: 3 POLE VS 4 POLE DISCONNECT

If there are any other processes that depend on this drive that would not be shut down the extra pole can be used as a safety to shut down them too if the handle is pulled. Example: A fiber blender that has a in feed conveyor that could jamb up if this drive went down because someone pulled the handle.
 