While I very seldom use one to test any outlets, polarity, etc. I know they cannot detect “bootleg ground”. At least the standard run of the mill ones.
Another thing I have found to be a problem is them to show having a effective ground, when in reality the actual egc (in this case beat up loose emt conduit) has a overall resistance of around 20ohms from EGC to neutral. We obviously know this will never clear a fault on a 20ampere circuit unless GFCI protected
Has anyone else ever noticed this?
Another thing I have found to be a problem is them to show having a effective ground, when in reality the actual egc (in this case beat up loose emt conduit) has a overall resistance of around 20ohms from EGC to neutral. We obviously know this will never clear a fault on a 20ampere circuit unless GFCI protected
Has anyone else ever noticed this?