Can a light be installed in a shower that will also have a steam generator?

Are there any special requirements for outlets above a hot water baseboard heat.

Is a Hot Water tank considered a continuous load?
 

rodneee

Senior Member
i say.... yes- no- yes.... but allow 1 hour on the phone with the inspector to find the code section for different requirements of hot water baseboard heat and electric baseboard heat.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
i say.... yes- no- yes.... but allow 1 hour on the phone with the inspector to find the code section for different requirements of hot water baseboard heat and electric baseboard heat.


There is no NEC code section for either, so I'm assuming that's why the phone call will take an hour. :)
 

N844AA

Member
Location
Los Angeles
Is a hot water tank really a continuous load? I don't have much experience with these but are the heating elements really energized continuously for 3 or more hours at a time?

This surprises me.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is a hot water tank really a continuous load? I don't have much experience with these but are the heating elements really energized continuously for 3 or more hours at a time?

This surprises me.

Yup, take a look at 422.13.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is a hot water tank really a continuous load? I don't have much experience with these but are the heating elements really energized continuously for 3 or more hours at a time?

This surprises me.
I would agree with you but
422.13 Storage-Type Water Heaters.
A fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall be considered a continuous load for the purposes of sizing branch circuits.
 

tkb

Senior Member
Location
MA
Is a hot water tank really a continuous load? I don't have much experience with these but are the heating elements really energized continuously for 3 or more hours at a time?

This surprises me.

As i was reading this thread, I was wondering the same thing until it was clairified.

yes-no-yes here too.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
...and I would say the answer is both yes and no. Yes, continuous [conditionally, I might add] in regards to branch circuit sizing, but no for Article 220 calculations.

Article 422.13 states for branch circuits. I agree no for calculations in art. 220.
 

mtfallsmikey

Senior Member
In the instructions that come with the heater.

As far as I know or remember, none of the HWBB we ever installed (Slant-Fin, Continental brands )ever had recommendations/specs for minimum spacing between the BB and receptacles. The water temps in BB can range between 130-180. As far as steam generators are concerned, we made sure that either we or the EC installed some type of sealed recessed light, not sure of what NEC would require.
 