I understand I had similar post before but at that time I was not sure about 3 tier series rating.
I have high rise that has bunch of meter stacks fed from switchboard with 65kaic rating. Meterstacks then feed individual resident panel.
Attached sketch shows one of the meterstacks fed from switchboard feeder breaker. No meters are shown at meter stacks for clarity. Meterstack has 22kAIC rating and so does the panelboards. There are 26 feeder breakers in the meter stacks which feed 26 dwelling unit panelboards that have HVAC load
Each dwelling unit panelboard has hvac load FLA of 16A. Assume their is 3-tier series rating between switchboard feeder breaker, meterstack feeder breaker and panelboard feeder breaker
I did trace fault current path, did calcs and sum of all motor FLA currents I got are greater then 1% of 22kaic at fault points F1,F2,F3 attached sketch. However I am not sure about it or if I did it correctly.
Assume their is fault at point F1, F2, or F3 attached sketch or at any other location then according to NEC 2017 section 240.86 one cannot do 3-tier series rating or any tier series rating? Would this be correct or incorrect?
I have high rise that has bunch of meter stacks fed from switchboard with 65kaic rating. Meterstacks then feed individual resident panel.
Attached sketch shows one of the meterstacks fed from switchboard feeder breaker. No meters are shown at meter stacks for clarity. Meterstack has 22kAIC rating and so does the panelboards. There are 26 feeder breakers in the meter stacks which feed 26 dwelling unit panelboards that have HVAC load
Each dwelling unit panelboard has hvac load FLA of 16A. Assume their is 3-tier series rating between switchboard feeder breaker, meterstack feeder breaker and panelboard feeder breaker
I did trace fault current path, did calcs and sum of all motor FLA currents I got are greater then 1% of 22kaic at fault points F1,F2,F3 attached sketch. However I am not sure about it or if I did it correctly.
Assume their is fault at point F1, F2, or F3 attached sketch or at any other location then according to NEC 2017 section 240.86 one cannot do 3-tier series rating or any tier series rating? Would this be correct or incorrect?
Last edited: