MomentumElectric
Member
- Location
- Oakland, CA
I'm trying to figure out how to hook-up (3) jobsite trailers to (1) 70kVA generator.
I'm pretty sure that the inspector is going to want to see (2) ground rods driven at each trailer, plus two at the generator.
I'm not sure, but I think I may need to run SE cable to a subpanel on a pole, and then run (3) mastheads out of the pole, and then (1) masthead into each of the trailers.
It seems like that's a lot of bullshit and a lot of copper to have overhead, but since the panels are 60A, it exceeds what the code allows for SOOW cord.
Even if I could run SOOW cord, could I run it on the ground from the generator?
The alternative would be to put a 50A breaker in each of the panels, and take out the 60A (see attached picture). I think this would allow me to avoid the mastheads and overhead wiring, but not the ground rods.
The codes I could find that apply to jobsite trailers are included in the first attached document "5958 Horton"
Here is the generator:
http://www.multiquip.com/multiquip/DCA70USI.htm
Thanks for any help with this.
I'm pretty sure that the inspector is going to want to see (2) ground rods driven at each trailer, plus two at the generator.
I'm not sure, but I think I may need to run SE cable to a subpanel on a pole, and then run (3) mastheads out of the pole, and then (1) masthead into each of the trailers.
It seems like that's a lot of bullshit and a lot of copper to have overhead, but since the panels are 60A, it exceeds what the code allows for SOOW cord.
Even if I could run SOOW cord, could I run it on the ground from the generator?
The alternative would be to put a 50A breaker in each of the panels, and take out the 60A (see attached picture). I think this would allow me to avoid the mastheads and overhead wiring, but not the ground rods.
The codes I could find that apply to jobsite trailers are included in the first attached document "5958 Horton"
Here is the generator:
http://www.multiquip.com/multiquip/DCA70USI.htm
Thanks for any help with this.