A/A Fuel GTX
- WI & AZ
- Electrician
I'm looking at 210.70 and don't see a requirement for 3 way switches in a residential hallway. Is it somewhere else or is there not a requirement?
And, technically, that switch need not even be in that room, nor by a door.The same with other types of rooms as well, you could have a living room with 4 entrances and all that the NEC requires is one wall switch controlled lighting outlet.
I always put three ways in hallways but I inherited a job that is already roughed in and rocked and no threes to be found.
You could fish in a dead end 3 way if attic above or simply do without.I always put three ways in hallways but I inherited a job that is already roughed in and rocked and no threes to be found.
Only location requirement that I'm aware of for three ways is 210.70(2)(c) but that is for more than six steps. 210.70 covers the whole issue.
Are dimming switches required in residential. Is there a code stating some sort of requirement if there is?
Some state and local energy codes require it, but nothing in the NEC.Are dimming switches required in residential. Is there a code stating some sort of requirement if there is?
4.Lighting other than in kitchens, bathrooms,
garages, laundry rooms and utility rooms. Permanently
installed luminaires located other than in kitchens,
bathrooms, garages, laundry rooms and utility
rooms shall be high efficacy luminaires.
Exception 1 to Section 150 (k) 4: Permanently
installed luminaires that are not high efficacy
luminaires shall be allowed, provided they are controlled
by a dimmer switch.
Exception 2 to Section 150 (k) 4:Permanently
installed luminaires that are not high efficacy shall be
allowed, provided that they are controlled by an occupant
sensor(s) certified to comply with Section 119
(d). Such motion sensors shall not have a control that
allows the luminaire to be turned on automatically or
that has an override allowing the luminaire to be
always on.