TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
I might or might not have a problem with a project starting Tuesday and want to be prepared. I may have to wire up a lighting circuit using 3-way switches in a Class I, Div II area. Am being supplied with 12-3 Okanite, rubber coated armored MC cable. Because of the classification , I cannot use the armor as the ground. I must use a wire conductor for the ground. That leaves me only two conductors in the cable. Am thinking it is possible to use two cables and not violate the NEC article about have all circuit conductors within the same raceway. I do not think this is possible with a standard 3-way wiring method with the hot going to the common of one switch and the light being fed from the common of the other, with the neutral going to the light of course.
But what if a California 3-way is used? One cable would have the neutral going to the light and the traveler that is landed on the commons of both 3-way switches. The other cable would have the Hot going to one contact of each switch and the Load wire on the other contact of each switch going to the light. The power cable would come to one switch, and the load cable going to the light from the other switch.
Feel free to laugh at the sketch. The way I see it is each cable of two conductors will have current flowing in opposite directions, making it either a switch leg, with two ungrounded conductors, or a complete branch circuit of one hot and one neutral, again flowing in opposite directions.
No need to mention an inspector. This is a gas compressor station. It just isn't done.
But what if a California 3-way is used? One cable would have the neutral going to the light and the traveler that is landed on the commons of both 3-way switches. The other cable would have the Hot going to one contact of each switch and the Load wire on the other contact of each switch going to the light. The power cable would come to one switch, and the load cable going to the light from the other switch.
Feel free to laugh at the sketch. The way I see it is each cable of two conductors will have current flowing in opposite directions, making it either a switch leg, with two ungrounded conductors, or a complete branch circuit of one hot and one neutral, again flowing in opposite directions.
No need to mention an inspector. This is a gas compressor station. It just isn't done.