3 way switches

Status
Not open for further replies.

gerry

Member
Location
New Jersey
Any ideas of what would cause 65 volts to be present at a light fixture connected to three ways , when the three ways are off. Is it normal to have leakage,if so what is allowed.Thanks for any infor.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 3 way switches

You say 65 volts with the 3 ways off, if so the lamp should be still glowing some, or are you mesuring the 65 volts with a digital meter with out the lamp conected.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: 3 way switches

If you are using a digital voltmeter, are you certain that the reading is not 65 millivolts (mv)? It would not be strange to see a stray voltage of 65mv, nor would it be a problem.

If it really is 65 V, then (1) Where are you taking your measurements (between what and what), and (2) How do you know that the 3-ways are "off"?
 

sparkyoh

Member
Location
Ohio
Re: 3 way switches

Had a similar problem recently, it was an open neutral on a multi-wire circuit, as a matter of fact I had 64 volts.
 
Re: 3 way switches

Originally posted by gerry:
Any ideas of what would cause 65 volts to be present at a light fixture connected to three ways , when the three ways are off. Is it normal to have leakage,if so what is allowed.Thanks for any infor.
A digital meter is sensitive enough that capacitive coupling between the one "hot" wire and a traveller can make it read that high. If the run is long enough (30 feet or so), you can get enough coupling to fire a neon test lamp. Place a small load across your meter leads and it should go away.
 

jeff clarke

New member
Re: 3 way switches

Similar to sparkyoh, I had an open neutral that produced 94 volts. Not enough to light a bulb(designed to produce energy at 120 volts) but enough to show up on an inductive voltage tester. With weird/low voltage problems it always pays to check for open neutrals.
 

big john

Senior Member
Location
Portland, ME
Re: 3 way switches

Disconnect the hot conductor to the fixture, open up the last switch before the fixture and test for voltage to ground on the switched common. If you have 65 volts to ground when the light should be off, you'll know your problem is somewhere before the fixture.

However, if everything checks out beautifully before the fixture, then start looking for neutral conductor troubles.

-John

[ November 17, 2003, 09:44 AM: Message edited by: big john ]
 