markebenson
Senior Member
- Location
- fl
Old Church In NC
Service was changed from 100a to 200a using a meter/main combo and the 100a feed from the power company remains!
2x 100 mains feed 2 separate panels.
Panel A has separate ground and neutral bars but the branch circuits have the ground and neutrals connected to the same bar.
Panel B has ground and neutral bonded.
A grounding rod has yet to be located.
My thoughts:
1. Re-terminate panels A and B properly and as non-bonded panels.
2. Verify / add grounding rods as required.
3. Have power company upgrade wiring and inspect connections / transformer at pole.
4. Upon completion test with power quality device.
Service was changed from 100a to 200a using a meter/main combo and the 100a feed from the power company remains!
2x 100 mains feed 2 separate panels.
Panel A has separate ground and neutral bars but the branch circuits have the ground and neutrals connected to the same bar.
Panel B has ground and neutral bonded.
A grounding rod has yet to be located.
My thoughts:
1. Re-terminate panels A and B properly and as non-bonded panels.
2. Verify / add grounding rods as required.
3. Have power company upgrade wiring and inspect connections / transformer at pole.
4. Upon completion test with power quality device.