I'm having a go around with an engineer over this (The project is running out of money)
We are installing a 3-phase, 480V, 100Amp receptacle in an outdoor location that is also Class 1 Div.1 (It's a long story...... the receptacle is in the classified area, the equipment is not.)
We are using Meltric DS200 pin and sleeve plug/receptacle. The receptacle is horsepower rated, and has two auxiliary pins for interlocking. These pins engage last, after the power pins are connected, and the assembly is designed to suppress arc flash.
The engineers design utilizes a 2 wire control circuit. The aux pins in the plug are shorted together at a terminal block in the portable device.
When the employee seats the plug in the receptacle, the control circuit is completed through the aux pins, and a contactor pulls in to supply power to the receptacle. The employee would be holding the metal case of the plug during this time.
The engineer maintains that since the plug is designed so that the power pins are seated first, and there is no arc flash danger, therefore two wire control is adequate. (like I said, we are over budget and the engineer does not want to spend the money for an explosion proof start/stop station)
My argument is:
1. Every high power cord and plug connected installation I have ever seen has 3-wire control. The employee seats the plug, then presses a start button to energize. Because this adds to cost, it must be a code requirement SOMEWHERE, otherwise no one would do it..
2. In addition to arc flash, there is electrocution danger, especially in an outdoor installation. So the 3-wire start/stop keeps the employee from handling an energized bologna cord. The employee seats the plug, lets go, then presses a start button
3. Since a ground fault in the plug could result in death, we need to reduce the risk as much as possible.
So far, I have looked at NEC, NFPA 79, OSHA and WAC (Washington Administrative Code- basically, local amendments to OSHA). I don't have access to UL 508.
The only thing I can find are OSHA and WAC regulations that say employees shall not handle energized cords with wet hands.
Does anyone know of a chapter and verse in an applicable code that will support my argument? Or is the engineer correct in saying 2-wire control is adequate?
We are installing a 3-phase, 480V, 100Amp receptacle in an outdoor location that is also Class 1 Div.1 (It's a long story...... the receptacle is in the classified area, the equipment is not.)
We are using Meltric DS200 pin and sleeve plug/receptacle. The receptacle is horsepower rated, and has two auxiliary pins for interlocking. These pins engage last, after the power pins are connected, and the assembly is designed to suppress arc flash.
The engineers design utilizes a 2 wire control circuit. The aux pins in the plug are shorted together at a terminal block in the portable device.
When the employee seats the plug in the receptacle, the control circuit is completed through the aux pins, and a contactor pulls in to supply power to the receptacle. The employee would be holding the metal case of the plug during this time.
The engineer maintains that since the plug is designed so that the power pins are seated first, and there is no arc flash danger, therefore two wire control is adequate. (like I said, we are over budget and the engineer does not want to spend the money for an explosion proof start/stop station)
My argument is:
1. Every high power cord and plug connected installation I have ever seen has 3-wire control. The employee seats the plug, then presses a start button to energize. Because this adds to cost, it must be a code requirement SOMEWHERE, otherwise no one would do it..
2. In addition to arc flash, there is electrocution danger, especially in an outdoor installation. So the 3-wire start/stop keeps the employee from handling an energized bologna cord. The employee seats the plug, lets go, then presses a start button
3. Since a ground fault in the plug could result in death, we need to reduce the risk as much as possible.
So far, I have looked at NEC, NFPA 79, OSHA and WAC (Washington Administrative Code- basically, local amendments to OSHA). I don't have access to UL 508.
The only thing I can find are OSHA and WAC regulations that say employees shall not handle energized cords with wet hands.
Does anyone know of a chapter and verse in an applicable code that will support my argument? Or is the engineer correct in saying 2-wire control is adequate?