3 wire for cables recessed lights

Status
Not open for further replies.

Rig84

Member
Location
Maryland
Occupation
Electrician
I have 26 recessed lights in a vaulted ceiling. They want every other light to be controlled by a separate switch. Can I just use 14-3 and make the fist one black, splice the red through, then make the second one red and splice the black through? These fixtures look so small, I’m not sure if I’ll be over on my conductor fill if I have (2) 3 wires at each light. They are the Lowe’s brand utilitech 6” fixtures. Should I just set a junction box at each light and use a separate 14- 2 wire-whip for each light?
 
If you use a JB will it be accessible? I would use a separate 14/2 for each switch and just alternate them.
 
It's been a while but the last Utilitech fixtures I check had the box fill requirement on the j box cover plate.
If 14/3 is allowable (it would be on the fixtures I saw), I would go that route.
 
If you use a JB will it be accessible? I would use a separate 14/2 for each switch and just alternate them.
I would do that, but I’m already maxed out on the switch box the wire is coming out of. (2) 2- wires would put me 1 over conductor fill.
 
It's been a while but the last Utilitech fixtures I check had the box fill requirement on the j box cover plate.
If 14/3 is allowable (it would be on the fixtures I saw), I would go that route.
These don’t have anything written on them. They are tiny though. Even if they were allowed, I’m thinking I’d have a hell of a time getting (2) 3 wires in each box.
 
If you use a JB will it be accessible? I would use a separate 14/2 for each switch and just alternate them.
That’s where I’m not sure. Is the 5-6” hole for the light considered to be accessible? I could put them right above where the fixture would go. The fixture only takes up 3” or so and it’s a 12” rafter. It is a vaulted ceiling, so not accessible from an attic
 
That’s where I’m not sure. Is the 5-6” hole for the light considered to be accessible? I could put them right above where the fixture would go. The fixture only takes up 3” or so and it’s a 12” rafter. It is a vaulted ceiling, so not accessible from an attic
You cannot put a junction box above the ceiling adjacent to the fixture. We used to do that if necessary but there was a code change that now prohibits it.
 
Are they planning on using dimmers on these lights? Many don't play well with a shared neutral between two dimmers so you're back to using separate 2-wire switch legs. If the switch box is too small then change it.
 
They said no dimmers for now, possibly down the road. Very difficult customers lol. So I have a 4 gang box with these switches, it’s the biggest 4-gang I could find at local supply house. There’s also a different switch for pendant lights, and one for a ceiling fan. My question is only about the 2 for the recessed lights. My dilemma is being able to get (2) 3 wire cables in each light. I thought about setting j-boxes at each light so I could drop a 2- wire to each light, but someone here said that is now prohibited. Anyone know the code section? The hole would be 6” and the box would be above it
 
My dilemma is being able to get (2) 3 wire cables in each light. I thought about setting j-boxes at each light so I could drop a 2- wire to each light
Are these new constructuon cans, remodel cans, wafer lights, or......?

Every new construction can I've seen will accept up to (8) #12 which would amount to (9) #14

Remodel cans typically have considerably smaller j-boxes, though.
 
My dilemma is being able to get (2) 3 wire cables in each light. I thought about setting j-boxes at each light so I could drop a 2- wire to each light, but someone here said that is now prohibited. Anyone know the code section? The hole would be 6” and the box would be above it
New in the 2020 NEC:
410.118 Access to Other Boxes.
Luminaires recessed in ceilings, floors, or walls shall not be used to access outlet, pull, or junction boxes or conduit bodies, unless the box or conduit body is an integral part of the listed luminaire.
 
Don't splice the unused conductor and then it only counts as one for the purpose of conduit fill. Also from a practical matter, it eliminates one connector in the box.
 
Don't splice the unused conductor and then it only counts as one for the purpose of conduit fill. Also from a practical matter, it eliminates one connector in the box.
Difficult to do through a single KO. (I'm guessing NM cable.)
 
Are these new constructuon cans, remodel cans, wafer lights, or......?

Every new construction can I've seen will accept up to (8) #12 which would amount to (9) #14

Remodel cans typically have considerably smaller j-boxes, though.
These are the flat wafer style lights. The j-box on them is tiny
 