sevlander
Member
- Location
- new jersey
We have an existing 3 wire delta utility service with the B phase connected to ground. The connection is made in the hot service trough with 2 disconnects fed off of it. Each disconnect switch only breaks A and C phase and the grounded B phase goes straight through and is taped white. We are changing out one of the disconnect switches and discovered this arrangement.
I believe should both of these switches be upgraded to 3 pole fused type switches breaking all 3 legs and the white ID tape should be removed. The B phase is grounded in the hot trough only and not anywhere beyond that and I believe this is correct. Does anyone agree or have thoughts?
My understanding of grounding one leg is to have a reference point for voltage readings only and serves no other purpose, is this correct? Thanks
I believe should both of these switches be upgraded to 3 pole fused type switches breaking all 3 legs and the white ID tape should be removed. The B phase is grounded in the hot trough only and not anywhere beyond that and I believe this is correct. Does anyone agree or have thoughts?
My understanding of grounding one leg is to have a reference point for voltage readings only and serves no other purpose, is this correct? Thanks