Went to look over a site today. Lady asked me not to run away! I took a quick look & saw why she had made the request.
"Friend buddy etc." were going to help them. Took plug & switches out. Put panel in clothes closet (would not have had code clearances to begin with). Junction boxes in narrow gas furnace closet. And that was the good stuff.
The structure was a garage (800 square feet) turned into dwelling. It is feed from a 200 amp overhead service that feeds main breaker feed-through panel, with a 125 amp breaker by way of overhead triplex. This panel also feeds the main house through the feed-through lugs, overhead with triplex.
One occupant complained about lights dimming, devices operating at partial speed, etc.. They were using electric space heaters, hair dryer, curling iron, microwave, etc.
The triplex [possibly #4] (have not done a load calculation yet, total electric) appears to be to small for the 125 breaker.
Is it permissible to stay with the 3 wire feeder & install 2 5/8"x8' ground rods (instead of the 1/2"x ?) and meet code in any way?
I will try to take pictures of some of the items before any work is done. Would be good for the "What is wrong here" article in a trade magazine, except it would take up all the space listing articles.
"Friend buddy etc." were going to help them. Took plug & switches out. Put panel in clothes closet (would not have had code clearances to begin with). Junction boxes in narrow gas furnace closet. And that was the good stuff.
The structure was a garage (800 square feet) turned into dwelling. It is feed from a 200 amp overhead service that feeds main breaker feed-through panel, with a 125 amp breaker by way of overhead triplex. This panel also feeds the main house through the feed-through lugs, overhead with triplex.
One occupant complained about lights dimming, devices operating at partial speed, etc.. They were using electric space heaters, hair dryer, curling iron, microwave, etc.
The triplex [possibly #4] (have not done a load calculation yet, total electric) appears to be to small for the 125 breaker.
Is it permissible to stay with the 3 wire feeder & install 2 5/8"x8' ground rods (instead of the 1/2"x ?) and meet code in any way?
I will try to take pictures of some of the items before any work is done. Would be good for the "What is wrong here" article in a trade magazine, except it would take up all the space listing articles.