Hello, I believe I have interpreted 250.140 correctly and provided the correct estimate for a job. However, I can't answer the question about why the code calls for this work or effectively describe the safety issue behind it.
I will helping on a job where we will install a Service Entrance ATS in a house built in the late 1980s. The load center will become a subpanel. The have 3 wire SEU cabling to the range and 3 wire NM cabling to the dryer.
The dryer is fine based on 250.140 exception (3) because the grounded conductor is insulated. The range has to be re-wired because that circuit will now originate at a subpanel and the grounded conductor is not insulated. (Personally, I would change the dryer out too because it's 2 feet away from the breaker panel but that's above my pay grade. It won't cost much.)
250.140 (3): “The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service entrance cable and the branch circuit originates at the service equipment.”
Is the issue that clearing a ground fault will now have to go through the subpanel to the ATS to reach an ECG? Does that put the devices downstream of the subpanel at risk? I can't wrap my head around the additional risk this creates terminating in a subpanel or why an insulated conductor makes a difference.
We're going to do all the work correctly either way but I would feel better just understanding the theory behind it.
Thanks
Bill
I will helping on a job where we will install a Service Entrance ATS in a house built in the late 1980s. The load center will become a subpanel. The have 3 wire SEU cabling to the range and 3 wire NM cabling to the dryer.
The dryer is fine based on 250.140 exception (3) because the grounded conductor is insulated. The range has to be re-wired because that circuit will now originate at a subpanel and the grounded conductor is not insulated. (Personally, I would change the dryer out too because it's 2 feet away from the breaker panel but that's above my pay grade. It won't cost much.)
250.140 (3): “The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service entrance cable and the branch circuit originates at the service equipment.”
Is the issue that clearing a ground fault will now have to go through the subpanel to the ATS to reach an ECG? Does that put the devices downstream of the subpanel at risk? I can't wrap my head around the additional risk this creates terminating in a subpanel or why an insulated conductor makes a difference.
We're going to do all the work correctly either way but I would feel better just understanding the theory behind it.
Thanks
Bill