3 wire s.e.r. from 200 amp disconnect to 200 distribution panel

Status
Not open for further replies.

nmbme

Member
So I have a home inspector telling me the grounds and neutrals need to be separated in the panel, because panel is away from meter base. The feeders are a 3 wire, ( two hots and bare neutral, no ground), this the s.e.r. 3 wire conductor. The way it was done back than was ,you would have the meter feeding a disconnecting means and the disconnecting means then would feed the panel. So, how do you separate grounds and neutrals without having to new wire ?
 
HIs are quite often wrong about issues where an installation was code compliant at the time it was installed but the codes have changed since that time.
If an installation was not compliant when installed there is no grandfathering and in most jurisdictions I believe the AHJ can require correction any time it comes to their attention.

Sent from my XT1585 using Tapatalk
 
  1. Is your service panel so far away from where the service wire enters the residence that there is a requirement by your local building/electrical department that a service disconnect is required? Panel distance from meterbase has no bearing.
  2. Although you have 3 wire cable running to your panel, it was very common before electricians realized it that 3 wire cable was ok to run between service disconnect and panel. So he may be correct.
  3. You also are sayin 3 wire SER when you mean SEU. SER cable has 2hots, 1neutral, 1bare ground wire within the jacket.
 
So I have a home inspector telling me the grounds and neutrals need to be separated in the panel, because panel is away from meter base. The feeders are a 3 wire, ( two hots and bare neutral, no ground), this the s.e.r. 3 wire conductor. The way it was done back than was ,you would have the meter feeding a disconnecting means and the disconnecting means then would feed the panel. So, how do you separate grounds and neutrals without having to new wire ?

The connection between the disconnecting means and the panel is as you've stated a feeder and would require 4 conductors (SER not 3 conductor SEU) and the neutrals and EGC's separated in the panel.

Sounds like the HI got this one right.
 
As Trevor stated you need 4 wires between the main disconnect and a sub panel. SER is 4 conductor (2 hots, neutral and a bare) while SEU is 3 conductor (2 hots and a bare ). Terminology is important.

If there is only a 3 wire cable going from the main disconnect to the sub panel then you need to rewire it.
 
It would have been and still would be pretty rare to be able to run SE cable to a separate building. The portion attached to either building could easily be SE cable but you very likely transition to a different wiring method for what is between the two buildings.

I guess if you had construction methods between multiple sections of one building that effectively made them separate buildings by code you could see SE cable used.
 