We have a customer that is asking us to provide branch/feeder circuits for approximately 70-75 KW of lighting load for an indoor grow facility in an existing building. Existing service main is 480 volt-3 phase 3 wire. Customer will provide luminaires (Cali special "m" grow operation with lights on for extended time periods - continuous duty). I am calling out for 277 volt ballasts on their 750/1000 watt HID (MH or HPS) fixtures. I would rather not get into the merits of one type of lighting over the other in this discussion; my customer is the expert.
I plan on generating a neutral on the existing system by installing either a 75/112.5 kva single transformer of auto zig - zagging 3 smaller xformers (3 x 10= 103.8kva as per acme electric).
I will then go to a 200 amp panelboard with a neutral bar; then to lighting contactor; then out to the grow rooms with 4 wire circuits. As per nec 20 14 table 210.24, 15 through 50 amp circuits may be used for 1000 watt HID fixtures, assuming that the mfg used heavy duty lampholders. (Watch for "Ch" import mfgs).
Please help me by commenting on the following:
1) Even though 50 amp conductors, #6 cu, could be used, I am reluctant to go that route. If we use 4 sq and 5 sq boxes, #6 could be unruly. Also, we could see a higher failure rate of connections of #6 to smaller tap wires. Disastrous if a neutral connection were to fail. I feel much more comfortable using #8-40 amp of #10-30 amp methods.
2) Using auto transformer zig zag connections to generate a neutral to get my 277 volts. More bang for the buck. Any chances of floating voltages? Seems like I read about some issues with zig-zags in a post. I cannot see going 120/208 because of the need for more circuits. Also, 208 circuits do not allow for multi-wire circuits.
3) At the ends of the runs and also where branches are made from the main runs, which tap rules would allow smaller wire usage for the smaller loads? It is tempting to hardwire fixtures. Table 210.21 (B)(2) gives direction if you go to cord-plug.
4) If we use 4 wire circuits for 3 277V circuits with a common neutral for feeding our grow lights, are 3 pole breakers required? That would make troubleshooting a shorted/faulted circuit quite challenging and also shut down a whole bunch of lights all at once.
Thank you!
I plan on generating a neutral on the existing system by installing either a 75/112.5 kva single transformer of auto zig - zagging 3 smaller xformers (3 x 10= 103.8kva as per acme electric).
I will then go to a 200 amp panelboard with a neutral bar; then to lighting contactor; then out to the grow rooms with 4 wire circuits. As per nec 20 14 table 210.24, 15 through 50 amp circuits may be used for 1000 watt HID fixtures, assuming that the mfg used heavy duty lampholders. (Watch for "Ch" import mfgs).
Please help me by commenting on the following:
1) Even though 50 amp conductors, #6 cu, could be used, I am reluctant to go that route. If we use 4 sq and 5 sq boxes, #6 could be unruly. Also, we could see a higher failure rate of connections of #6 to smaller tap wires. Disastrous if a neutral connection were to fail. I feel much more comfortable using #8-40 amp of #10-30 amp methods.
2) Using auto transformer zig zag connections to generate a neutral to get my 277 volts. More bang for the buck. Any chances of floating voltages? Seems like I read about some issues with zig-zags in a post. I cannot see going 120/208 because of the need for more circuits. Also, 208 circuits do not allow for multi-wire circuits.
3) At the ends of the runs and also where branches are made from the main runs, which tap rules would allow smaller wire usage for the smaller loads? It is tempting to hardwire fixtures. Table 210.21 (B)(2) gives direction if you go to cord-plug.
4) If we use 4 wire circuits for 3 277V circuits with a common neutral for feeding our grow lights, are 3 pole breakers required? That would make troubleshooting a shorted/faulted circuit quite challenging and also shut down a whole bunch of lights all at once.
Thank you!