30 A /120V single phase receptacle for motor home hookup at residence
jonbeme
moreno valley
120/240v singlephase 100 amp service
run length 60 ft from panel
having hard time finding code for installation
simple right!! wire sizing per NEC ???
im just having a major brain fart!!!
please someone walk me through again
do i need a disconnect for receptacle??:)
Start by looking at Article 550 and let us know what piece of the puzzle you're missing.
Welcome to the Forum. :)
I don't see how Article 550 applies to a receptacle for a motor home. I expect you intended to reference Article 551, but I don't think that applies either. Just the normal Chapter 1-4 rules that cover receptacle outlets would apply to this instalaltion.
If I filled in the blanks correctly your 60 ft run poses no voltage drop problem with #10 wire.
What is your concern ?
You might be right. I probably misread this as a question for a mobile home under Article 550.
Jonbeme, just to be sure and so I didn't send you on a wild goose chase, is this a mobile home or a motor home? If it's the latter, disregard my first reply and read Don's reply.
551.2 definitions say that an RV park has two or more RV sites. If OP is only supplying one RV he does not have an RV park and therefore ch 1-4 wiring methods are what determines how to do this install.
The only things in 551 that apply in this case is internal to the RV and outside the scope of the OP.