PEstimator
Member
- Location
- Houston, Texas
I been told that I can not install 30A breaker on a Lighting circuit other than 20A
NEC 210.21(A) talks that when a Lampholder is connected to a circuit rated above 20A, the lampholder shall be of the Heavy-Duty type. not less than 660W or 750W depending of the material.
I think this was written for the use of the old style Metal Halide or High Pressure Sodium Lamps.
And this the exception on NEC 210.23(B) as long the load does not exceed 80 percent of the branch-circuit ampere rating.
My question is: where the T5HO (6 or 8 lamps) and LED (150W to 350W) high bays stand? Those can not be called Heavy Duty?
Are these called equal to Metal Halide lamps not allowed to be on 30A breaker with #10 AWG wire?
Please help me out & thanks in advance.
NEC 210.21(A) talks that when a Lampholder is connected to a circuit rated above 20A, the lampholder shall be of the Heavy-Duty type. not less than 660W or 750W depending of the material.
I think this was written for the use of the old style Metal Halide or High Pressure Sodium Lamps.
And this the exception on NEC 210.23(B) as long the load does not exceed 80 percent of the branch-circuit ampere rating.
My question is: where the T5HO (6 or 8 lamps) and LED (150W to 350W) high bays stand? Those can not be called Heavy Duty?
Are these called equal to Metal Halide lamps not allowed to be on 30A breaker with #10 AWG wire?
Please help me out & thanks in advance.