The contactor will have data saying it must be protected by an OCPD not greater than its maximum rating. So from that standpoint, you are using it in a manner beyond its intended use. Change the breaker to 30A or change the contactor to 40A.
seems to me that the breaker probably would hold at 33.75 amps anyway. A breaker change is not the solution in my opinion you are still overloading a 30 amp device or devices both the breaker and the contactor. get a contactor rated 40 amps or higher for the correct solution or maybe you can shift some loads to get what you need and not overload this system.