davedottcom
Senior Member
Customer wants a 20 amp / 240V single receptacle for a Cigarette rolling machine! (Compressor)
The machine manufacturer asks for a 2-pole 30 amp breaker to be installed on the 20 amp/ 240V receptacle!?
The service is 3-phase 208V/120V.
Is this permitted, as long as the wire is rated for 30 amps? (#10)
The machine manufacturer asks for a 2-pole 30 amp breaker to be installed on the 20 amp/ 240V receptacle!?
The service is 3-phase 208V/120V.
Is this permitted, as long as the wire is rated for 30 amps? (#10)