New construction, major grocery chain. Commercial meat grinder, 8.5hp, comes with L15-30 plug on #8 awg SO cord. We're going to run an SO cord with connector from fused disconnect to the provided cord plug so that the unit can be disconnected and moved for cleaning.
I figure OCPD size to be 67.1 amps, max. The panel schedule calls for 50/3 breaker.
Lead journeyman says can't have 30 amp cord plug on 50 amp breaker (thinking possibly of 210.21.B.1?); my thought was that the cap is OK because the 50 amp breaker is for startup current, and the wire is protected by the fused disconnect, which I figured should be 37.5 amps (data plate shows 30 amps).
Should we put a bigger plug on the cord? To add confusion to the issue, the plans call for #10 wires from the panel.
(My amps figures comes from extrapolataing T450.250 since it jumps from 7.5hp to 10 hp; I got 26.84 for the amperage for an 8.5hp motor.)
I figure OCPD size to be 67.1 amps, max. The panel schedule calls for 50/3 breaker.
Lead journeyman says can't have 30 amp cord plug on 50 amp breaker (thinking possibly of 210.21.B.1?); my thought was that the cap is OK because the 50 amp breaker is for startup current, and the wire is protected by the fused disconnect, which I figured should be 37.5 amps (data plate shows 30 amps).