coming from a fused 100 amp knife disconnect fused at 80 amps i have a 240 100 amp plug wired with #2 awg wire also i wired a 30 amp plug W/ 10 awg
both are 3 phase ive been told i am not in code because the 80 amp fuses are too big . ive thought because you cant plug anything larger than 30 amps into the receptical 10 awg wire is ok do i need overload protection at 30 amps also?