30 AMP RV RECEPTACLE

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
Inspector wants gfci on 30 amp rv receptacle .the receptacle will mounted on side of house next to driveway with in use cover ?
 
Inspector wants gfci on 30 amp rv receptacle .the receptacle will mounted on side of house next to driveway with in use cover ?

Always good to know what the inspector wants. ;)

Did the inspector tell you it is required?

As far as I know the NEC does not require a GFCI for that application.
 
30 amp rv

30 amp rv

After talking with the again asking for code reference he changed his mind. ( SAD) THANKS FOR THE REPLY.
 
Do you have a code section for that?

I'd presume this is 120V and not 240V, tho I'm not aware of any current (2014 or older) code that would allow that circuit to not be GFCI protected. Is it because it is not a 15/20A receptacle?

Until 2017 outdoor recpts more than 20A and more than 120V did not require GFCI protection. Now almost all do, including 480/277V.
 
Status
Not open for further replies.
Top