My understanding is wire temp is a combination of ambient and heat produced by current and when calculated some things did not seem to add up.
For a residential house lets say ambient temp 30c and there is a situation that requires temp correction like a superhot attic 115f using RHW cable 75c column
310.15B16 #3awg copper RHW is 100 amp correction .75 from 310.15(B)(2)a 100*.75=75 amp.
For a normally hotter place like a factory with temp of 40c same situation
310.15B16 #3awg copper RHW is 100 amp correction .85 from 310.15(B)(2)b 100*.85= 85amp
So this is telling me under higher ambient temp i can put more current on conductor?????
There has to be a factor I'm missing help???????