Back in the 2005 NEC an ampacity adjustment was added regarding NM cables use through fire stopped or draft stopped holes. The requirement was to derate those cables. Problem was that 310.15(A)(2)Ex made that new requirement unenforceable. In the 2008 NEC, 334.80 contains new wording that explicitly prohibits applying the 310.15(A)(2)exception to this type of installation. Until they add similar wording to Article 376, 310.15(A)(2)Ex can be applied to wireways with more than 30 CCC's.