shawnbebout
Member
all,
Thank you for reading this and taking the time to educate me. We recently purchase a fluke 1736 data logger. Mainly to ensure our loads our balanaced in our facility, but I know they will be asking me how much I can add to the panel. I have completed a 4 day load study to use the information as a training tool, and I will attach a screen shot as a reference. Now I did have the interval set @ 5 seconds, not 15 minutes as spec out in 220.87. I think the loads are pretty well balanced. 120/208 volt 400 amp panel. Industrial panel. 3 phase 4 wire.
So in theory, if it was a 15 minute interval instead of a 5 second.
400 amp minus 110 max equals 290 amps. 290 divided by 1.25 equals 232 amps. So the max amount of loads I could add to this panel would be 232 amps.
Is my formula right?
Thank you for reading this and taking the time to educate me. We recently purchase a fluke 1736 data logger. Mainly to ensure our loads our balanaced in our facility, but I know they will be asking me how much I can add to the panel. I have completed a 4 day load study to use the information as a training tool, and I will attach a screen shot as a reference. Now I did have the interval set @ 5 seconds, not 15 minutes as spec out in 220.87. I think the loads are pretty well balanced. 120/208 volt 400 amp panel. Industrial panel. 3 phase 4 wire.
So in theory, if it was a 15 minute interval instead of a 5 second.
400 amp minus 110 max equals 290 amps. 290 divided by 1.25 equals 232 amps. So the max amount of loads I could add to this panel would be 232 amps.
Is my formula right?