This questions is with reference to the following thread:
http://forums.mikeholt.com/showthread.php?t=122067&page=2
If we follow the NEC tables the maximum overcurrent protection settings can be set. However if we plot the transformer damage curve with the protective devices and the transformer the transformer (esp. the overload or low fault current range) is not protected. This is particularly true for transformers with Delta - Star solidly grounded transformers, for which the transformer damage curve needs to be shifted to the left by 58%.
Is this typical to have, or is there a better way to protect than using molded case thermal magnetic CBs. The transformers under consideration are 30 kVA or 45 kVA, which I guess are not that expensive to replace and possibly in a commercial setting are unlikely to get overloaded, although the possibility of single line to ground fault cannot be ruled out.
Thank you.
http://forums.mikeholt.com/showthread.php?t=122067&page=2
If we follow the NEC tables the maximum overcurrent protection settings can be set. However if we plot the transformer damage curve with the protective devices and the transformer the transformer (esp. the overload or low fault current range) is not protected. This is particularly true for transformers with Delta - Star solidly grounded transformers, for which the transformer damage curve needs to be shifted to the left by 58%.
Is this typical to have, or is there a better way to protect than using molded case thermal magnetic CBs. The transformers under consideration are 30 kVA or 45 kVA, which I guess are not that expensive to replace and possibly in a commercial setting are unlikely to get overloaded, although the possibility of single line to ground fault cannot be ruled out.
Thank you.