I have to take a test for school and here is what I know. It’s a 480 - 120/208 Y 3 phase transformer to be sized for continuous load.
It’s a 30 KVA Transformer is primary overload I came up with 45 amps or just use a 40amp breaker (they give you a 30 a 40 and a 50) using #8 wire. Now the secondary i’m coming up with 104 amps so a 100 amp breaker, using #3 copper. It’s in FMC and I’m not sure if it’s going to be 24” or under where I would not need to derate the conductors. But my question is do I need to up the size of the wire because of the code saying under 100 amp needs to be sized to 60 degrees? Any input? I think I have this all figured out.
edit if i do have to derate and use 60c column then my #8 is still fine derated for 40amps but my secondary would have to be #1 which is 150 at 90c derated by 80% is 120 ( and at 60 is good for 110)
It’s a 30 KVA Transformer is primary overload I came up with 45 amps or just use a 40amp breaker (they give you a 30 a 40 and a 50) using #8 wire. Now the secondary i’m coming up with 104 amps so a 100 amp breaker, using #3 copper. It’s in FMC and I’m not sure if it’s going to be 24” or under where I would not need to derate the conductors. But my question is do I need to up the size of the wire because of the code saying under 100 amp needs to be sized to 60 degrees? Any input? I think I have this all figured out.
edit if i do have to derate and use 60c column then my #8 is still fine derated for 40amps but my secondary would have to be #1 which is 150 at 90c derated by 80% is 120 ( and at 60 is good for 110)