Hello, Got a service call, and was told the ternate got a shock while touching the hot water, and the metal enclosure for the dryer receptacle. 10 days prior some one got shocked putting in a new metal kitchen sink. So I saw I was getting 30volts from a Metal enclosure to the hot water pipe. Found it was the Hot water tank causing the issue. Then decided to look how the building bonding of the water pipe was done. There was none
So i have this, The Main metal underground water pipe is Split to feed the house. Then branches off and goes under ground(more then 10 feet) to feed a garage
The hot water outlet then comes in and feeds a PVC T pipe and runs next to the Cold water to feed the garage. By the looks of it, the cold water use to be an outside facet. Then they built a garage over, and added the hot water line in PVC.
So The garage is were I have an issue. The hot water is stubbed up with metal piping next to the cold. The cold is bonded but the hot is not.
So I am wondering does that stub 250.104 (A)(1) constitute a Metal Water Piping System. Do I have to run and bonding jumper all the way to that 28" stub..
I don't think it part of they system any more since it has 20 feet of PVC between metal parts.
There is no panel or disconnect in the garage, just 3-4 circuits ran in pipe over to it
I bounded The piping system under the house.
So i have this, The Main metal underground water pipe is Split to feed the house. Then branches off and goes under ground(more then 10 feet) to feed a garage
The hot water outlet then comes in and feeds a PVC T pipe and runs next to the Cold water to feed the garage. By the looks of it, the cold water use to be an outside facet. Then they built a garage over, and added the hot water line in PVC.
So The garage is were I have an issue. The hot water is stubbed up with metal piping next to the cold. The cold is bonded but the hot is not.
So I am wondering does that stub 250.104 (A)(1) constitute a Metal Water Piping System. Do I have to run and bonding jumper all the way to that 28" stub..
I don't think it part of they system any more since it has 20 feet of PVC between metal parts.
There is no panel or disconnect in the garage, just 3-4 circuits ran in pipe over to it