normbac

Senior Member
Wanted to get some clarity on mc support in a tbar ceiling with drop in panels 330.30 says 6ft max for no support and connectors may be used at luminare for support. If the distance between fixtures was 8 ft 300.11 says need support wire independent of grid . Question: can the connector still be used as support for the 1 ft within fixture requirement, if using a support wire in the center of the 8ft mc run.
Questing 2 : would a tbar with drywall be excluded form 330.30 since it is not accesible throughout. (Only accesible at a few location)
Can connectors be used as support.
Wasn't sure if heavy duty tbar that is used for drywall applied to all codes for tbar drop in ceilings. Thanks!
 

electricalist

Senior Member
Location
dallas tx
I think you are correct with question 1. although i find that since you will probably need a ceiling wire at each end of the fixture, you can bat wing the mc there and be close enough for most inspectors on the 1 ft rule and its 6 ft from light to light if the ceiling is accessable. The handbook shows ac cable laying on the grid from light to light with no securing but I wouldnt advise it . A inspector here would blow a gasket if he saw ac cable laying everywhere..
 