Is the requirement to identify the additional wires used for cable/fixture support above a ceiling grid a change in the '08? Or is it somewhere else in the '05 that I'm not finding? Thanks.
(1) Fire-Rated Assemblies Wiring located within the cavity of a fire-rated floor–ceiling or roof–ceiling assembly shall not be secured to, or supported by, the ceiling assembly, including the ceiling support wires. An independent means of secure support shall be provided and shall be permitted to be attached to the assembly. Where independent support wires are used, they shall be distinguishable by color, tagging, or other effective means from those that are part of the fire-rated design.
(2) Non?Fire-Rated Assemblies. Wiring located within
the cavity of a non?fire-rated floor?ceiling or roof?ceiling
assembly shall not be secured to, or supported by, the ceiling
assembly, including the ceiling support wires. An independent
means of secure support shall be provided and
shall be permitted to be attached to the assembly. Where
independent support wires are used, they shall be distinguishable
by color, tagging, or other effective means.
They obviously require the same means of ID as high-leg conductors.Where independent support wires are used, they shall be distinguishable by color, tagging, or other effective means.