300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened in place. Support wires that do not provide secure support shall not be permitted as the sole support. Support wires and associated fittings that provide secure support and that are installed in addition to the ceiling grid support wires shall be permitted as the sole support. Where independent support wires are used, they shall be secured at both ends. Cables and raceways shall not be supported by ceiling grids.
(1) Fire-Rated Assemblies. Wiring located within the cavity of a fire-rated floor?ceiling or roof?ceiling assembly shall not be secured to, or supported by, the ceiling assembly, including the ceiling support wires. An independent means of secure support shall be provided. Where independent support wires are used, they shall be distinguishable by color, tagging, or other effective means from those that are part of the fire-rated design.
Exception: The ceiling support system shall be permitted to support wiring and equipment that have been tested as part of the fire-rated assembly.
Wiring methods of any type and all luminaires are not allowed to be supported or secured to the support wires or T bars of a fire-rated ceiling assembly unless the assembly has been tested and listed for that use. If support wires are selected as the supporting means for the electrical system within the fire-rated ceiling cavity, they must be distinguishable from the ceiling support wires and they must be secured at both ends.
Generally, the rule for supporting electrical equipment is ?securely fastened in place.? This phrase means not only that vertical support for the weight of the equipment must be provided but also that the equipment must be secured to prevent horizontal movement or sway. The intention is to prevent the loss of grounding continuity provided by the raceway that could result from horizontal movement.
Sections 300.11(A)(1) and (A)(2) are quite similar. Unless the exceptions apply, these sections clearly prohibit all types of wiring from being attached in any way to the support wires of a ceiling assembly. Unless ceiling grids are part of the building structure, they, too, are prohibited from furnishing support for cables and raceways. However, if wiring and equipment are located within the ceiling cavity and rigidly supported independent of the ceiling, without the use of ceiling-type hanger wire, then the requirements of this section are met.
Refer to the appropriate wiring method article in Chapter 3 of the Code for cable and raceway supporting requirements. See 410.15(A) and 410.16 for the proper support of luminaires; 314.23 for the support of outlet boxes; and 725.6, 760.6, and 770.8 for various low-voltage fire alarm and optical fiber cable supports. See Chapter 8 for communications cable supports.
FPN:One method of determining fire rating is testing in accordance with NFPA 251-1999, Standard Methods of Tests of Fire Endurance of Building Construction and Materials.
(2) Non?Fire-Rated Assemblies. Wiring located within the cavity of a non?fire-rated floor?ceiling or roof?ceiling assembly shall not be secured to, or supported by, the ceiling assembly, including the ceiling support wires. An independent means of secure support shall be provided.
Exception: The ceiling support system shall be permitted to support branch-circuit wiring and associated equipment where installed in accordance with the ceiling system manufacturer?s instructions.