300.13 B in multi wire branchy circuit... so i could use receptacle to make and break the circuit in 2 wire installation?
 
Not sure what you asking, but for a receptacle, the grounded neutral is pigtailed (if there is an in and out). You can't wire two neutrals on the receptacle.
 
300.13 B in multi wire branchy circuit... so i could use receptacle to make and break the circuit in 2 wire installation?
Yes, in a two wire circuit both the grounded and ungrounded conductors pose the same hazard if opened, in a MWBC the neutral being broken while current is flowing is a different story.

Roger
 
The difference is that a shared neutral may not be de-energized when someone thinks it is, especially before the handle-tied breaker requirement.
 
I understand. most AHJ in our area will make you pig tail wiring in j box for wall cover. I always assumed because of that you couldnt use the receptacle as a make or break for circuit. Thanks
 