Yes, because there is only one hot wire dependent on the neutral at that point.300.13 B in multi wire branchy circuit... so i could use receptacle to make and break the circuit in 2 wire installation?
Yes, in a two wire circuit both the grounded and ungrounded conductors pose the same hazard if opened, in a MWBC the neutral being broken while current is flowing is a different story.300.13 B in multi wire branchy circuit... so i could use receptacle to make and break the circuit in 2 wire installation?
Obviously, their personal preference, and may be a holdover from when we were more freely allowed MWBC.I understand. most AHJ in our area will make you pig tail wiring in j box for wall cover. I always assumed because of that you couldnt use the receptacle as a make or break for circuit. Thanks