Does the NEC specifically require a fill adjustment for these pads?What about box fill?
While the NEC does not specifically address a fill adjustment for the pads, box fill is based upon the area of space given in table 314.16 A. IMHO if any material of any kind is inserted in the box then the minimum volume of the box would have to be recalculated.Does the NEC specifically require a fill adjustment for these pads
How would one determine how many conductors to deduct for the pad? I see nothing in the NEC that requires an adjustment when using these pads. That's not to say that in the future there won't but until then.While the NEC does not specifically address a fill adjustment for the pads, box fill is based upon the area of space given in table 314.16 A. IMHO if any material of any kind is inserted in the box then the minimum volume of the box would have to be recalculated.
While the NEC does not specifically address a fill adjustment for the pads, box fill is based upon the area of space given in table 314.16 A. IMHO if any material of any kind is inserted in the box then the minimum volume of the box would have to be recalcul
Thats a great point.How would one determine how many conductors to deduct for the pad? I see nothing in the NEC that requires an adjustment when using these pads. That's not to say that in the future there won't but until then.![]()
Measure the volume of the pad as per Archimedes, then subtract that from the volume of the box.How would one determine how many conductors to deduct for the pad?
There are several ways to do it but my question is why bother when it's not required.Measure the volume of the pad as per Archimedes, then subtract that from the volume of the box.
Cheers, Wayne
Well, at the very least it's a non-metallic barrier, so if its volume is not marked, you should deduct 1.0 in^3. If the thickness is only 1/16", that would be about right, anyway.There are several ways to do it but my question is why bother when it's not required.![]()