Question 1: From this code reference, Can multiple sections of Flexible Metal Conduit (<4' each) be installed?
Question 2: From this code reference, Is there a length limitation for MC cable?
Question 3: Is there any exceptions where liquidtight (LFMC) can be installed in a plenum per UL (#1995) or NFPA 90A?
300.22-
(B) Ducts or Plenums Used for Environmental Air Only wiring methods consisting of Type
MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without
an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate
metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in
ducts or plenums specifically fabricated to transport environmental air. Flexible metal conduit
shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable
equipment and devices.................................
Question 2: From this code reference, Is there a length limitation for MC cable?
Question 3: Is there any exceptions where liquidtight (LFMC) can be installed in a plenum per UL (#1995) or NFPA 90A?
300.22-
(B) Ducts or Plenums Used for Environmental Air Only wiring methods consisting of Type
MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without
an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate
metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in
ducts or plenums specifically fabricated to transport environmental air. Flexible metal conduit
shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable
equipment and devices.................................