300.3(b)

Status
Not open for further replies.

MasterDic

Member
Location
SoCal
a little input here please. so the discussion goes, your neutral has to go with your ungrounded conductors down to the switch, yes it does, no it dont, so forth and so on. article says nothing specific but mentions exceptions and that not being one of them, it also throws in the where used. any outside interpretations please, seems like a slightly grey loophole that needs to be cleared up.
 
MasterDic said:
so the discussion goes, your neutral has to go with your ungrounded conductors down to the switch, yes it does, no it dont, so forth and so on.

The neutral only has to go to the switch if used at the switch.

Read 300.3(B) and you see it says "where used".
 
Read the section and note where it says "where used".

A "hot" wire from a lighting outlet to a switch with a "switch leg" going back to the lighting outlet does not use a grounded conductor. There is no requirement for the grounded conductor to go to a switch location in this instance.

In other instances, the neutral may need to go through the switch box. The whole point is to have the magnetic fields cancel with the same current going one way as is coming back in an individual raceway or cable.

I think another code section deals with that but am too lazy to look it up right now.
 
thats the grey area im trying to clear up and get outside info on is the "where used" is thrown in there. this and a few other topics became a quite lengthy discussion between a pm and i and im just trying to get others opinions on this issue.
 
MasterDic said:
thats the grey area im trying to clear up and get outside info on is the "where used" is thrown in there. this and a few other topics became a quite lengthy discussion between a pm and i and im just trying to get others opinions on this issue.


Why don't you tell us exactly what the situation is and you might get a

better answer. If you are installing a device at the switch location that is

going to require the 'neutral' , then you must supply it.
 
From a Mike Holt Newsletter.

Induction. Where metal raceway (or metal-clad cable) contains the conductors for switches, arrange the wiring to avoid inductively heating the surrounding metal. To accomplish this, run all conductors of a given circuit in the same raceway [300.3(B) and 300.20(A)]. Note the exception, though-a grounded (neutral) conductor is not required in the same raceway or cable with travelers or switch leg (switch loops) conductors.

The entire page can be seen HERE
 
this is not an nec issue, but it should be noted that although the neutral may technically not be required with travellers, not installing the neutral with the travellers can often be associated with unwanted emf (ie. running the neutral with the travellers can reduce undesired flux)
 
nakulak said:
this is not an nec issue, but it should be noted that although the neutral may technically not be required with travellers, not installing the neutral with the travellers can often be associated with unwanted emf (ie. running the neutral with the travellers can reduce undesired flux)

That is only true is your doing something very unusal.

The common ways of wiring 3 ways without a neutral still balance each other out and there will be no EMFs running around the home. :smile:
 
Last edited:
Getting back to the OP's question, some switches such as; low voltage dimmers, motion switches, etc. require a neutral wire. This would be when you need to put a neutral wire at the switch. It is becoming more common to see special type switches like this in residential. The 2 ways of wiring that are most common are,
1) run the line conductors to the light box, then drop down to the switch with a 2 wire NM "hot & switch leg" no neutral wire.
2) run the line conductors to the switch box, then an NM "switch leg, neutral, & ground" to the light.
Both methods work and are code compliant. The second method gives you a neutral at the switch, the first method does not.
Personally I go with the neutral to the switch box, if you don't need it for the switch it hasn't cost you any more work, if you do need it you will be glad you put it there.
 