Hi,
I am trying to figure out alternative way to power multizone heating in hazardous area Class 1 Div 2 involving hydrogen gas. One of the solution was to use flexible custom made multicore cable as there are 5 three phase circuits to energize. The cost of this solution was too high and upon reading 300.3(C)(1), I believe it would be alright to bundle / sleeve single cores altogether.
The problem is NEC does not specify what appropriate way to do it. I don't see any restriction in article 500 and 501.
Any help would be appreciated.
L
I am trying to figure out alternative way to power multizone heating in hazardous area Class 1 Div 2 involving hydrogen gas. One of the solution was to use flexible custom made multicore cable as there are 5 three phase circuits to energize. The cost of this solution was too high and upon reading 300.3(C)(1), I believe it would be alright to bundle / sleeve single cores altogether.
Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
The problem is NEC does not specify what appropriate way to do it. I don't see any restriction in article 500 and 501.
Any help would be appreciated.