noonan
Member
- Location
- Bucks County, PA
- Occupation
- Project Manager
I have a situation where the previous owner of our site installed a 480V generator feeder (600V insulation) in the same manhole as MV (13.8kV)
feeders. At first, we thought this was a violation, but one of our consulting
engineers indicated it is not.
300.3.C.2.
(e) In manholes, if the conductors of each system are permanently and effectively separated from the conductors of the other systems and securely fastened to racks, insulators, or other approved supports, conductors of different voltage ratings shall be permitted.
My question is, what does "effectively separated" mean. Does it need to be a barrier or can physical space be the separation?
feeders. At first, we thought this was a violation, but one of our consulting
engineers indicated it is not.
300.3.C.2.
(e) In manholes, if the conductors of each system are permanently and effectively separated from the conductors of the other systems and securely fastened to racks, insulators, or other approved supports, conductors of different voltage ratings shall be permitted.
My question is, what does "effectively separated" mean. Does it need to be a barrier or can physical space be the separation?