I was looking thru some residential videos of installs and inspections, i seen a couple things i had questions on that i could not resolve regarding bored holes and restrictions
1. Large home an individual neatly ran many NM cables at least 15 from what i could see thru 2-9/16" holes for many ceiling joists (looked like very long hallway) for a large home. The NM cables were not bundled with tie wraps between ceiling joists but all went thru many ceiling joists together, at least 10 that i can see he was very proud of the neatness and called attention to it.
Would this arrangement require the adjustment factors of 310.15(B)(3)(a) ?
Is there any max hole size? there was more than 1-1/4" of wood beyond holes
2. Another situation an individual said no more than NM cables in a bored hole. I could not find a code reference to support. Does anyone know where this limitation would be in code? If it exists?
3. the only limits I really seen involving bored holes were the 1-1/4" requirements of 300.4 is there any others you could point me to that I should be aware of?
Thanks as always for your input it is appreciated
1. Large home an individual neatly ran many NM cables at least 15 from what i could see thru 2-9/16" holes for many ceiling joists (looked like very long hallway) for a large home. The NM cables were not bundled with tie wraps between ceiling joists but all went thru many ceiling joists together, at least 10 that i can see he was very proud of the neatness and called attention to it.
Would this arrangement require the adjustment factors of 310.15(B)(3)(a) ?
Is there any max hole size? there was more than 1-1/4" of wood beyond holes
2. Another situation an individual said no more than NM cables in a bored hole. I could not find a code reference to support. Does anyone know where this limitation would be in code? If it exists?
3. the only limits I really seen involving bored holes were the 1-1/4" requirements of 300.4 is there any others you could point me to that I should be aware of?
Thanks as always for your input it is appreciated