300.4 (e)
gunpowder
Glen Rock, Pa
The section states protection is to be provided against damage from roof replacement. If the roof is concrete above the steel decking, does the article apply? Is there a firm argument either way, or is it up the ahj?
Thanks
That section pertains to metal-corrugated roof decking which uses penetrating screws or other hold down devices not a concrete slab.
300.4(E) Cables, Raceways, or Boxes Installed in or Under
Roof Decking. A cable, raceway, or box, installed in ex-
posed or concealed locations under metal-corrugated sheet
roof decking
, shall be installed and supported so there is not
less than 38 mm (1 1 ⁄ 2 in.) measured from the lowest surface of
the roof decking to the top of the cable, raceway, or box. A
cable, raceway, or box shall not be installed in concealed lo-
cations in metal-corrugated, sheet decking–type roof.
Informational Note: Roof decking material is often repaired
or replaced after the initial raceway or cabling and roofing
installation and may be penetrated by the screws or other me-
chanical devices designed to provide “hold down” strength of
the waterproof membrane or roof insulating material.
I have never understood why the roof guys need 6"-8" screws to get through a 3" roof.
Corrugation difference between the peak and valley, and the varying insulation thickness to give the roof its 1 degree drainage. Not worth the effort to use diverse screws and survey each position for if it is a peak or valley, and how thick the insulation is tapered.
I was told that there was actually a minimum amount the screws have to extend through the entire roof. I never saw that in writing, I was told that by one of the guys doing it on a job I was working.
Asking the Almighty, better known as a Google search, comes up with a value of 3/8" to 2 1/2" depending on roof materials and fasteners.
I understand that roofers prolly use screws a bit long for CYA, it just seems to me that many times the extra length is really, really overkill. Prolly just me.