When did the NEC start requiring an "Insulated" bushing to be installed on a SE cable fitting.?
I just got a red tag for a 4/0 4/0 4/0 4 awg SE cable entering a disconnect through a UL listed NM type 2" connector that has a well rounded throat. But it is just not insulated. Would the Insulation on the SE cable count for the insulation?
I have never been giged for this before.
The inspector did say if I could find the reason in the NEC that would allow it without having a insulated throat he would remove the tag. but I can't find anything that would?