- Location
- New Jersey
- Occupation
- Journeyman Electrician
Had an inspector tell me that he requires conduits and direct burial cables to be placed on a bed of sand due to 300.5(F). His argument is that you would not know if the fill (regular old dirt removed from the trench) is corrosive. Has anyone ever heard of such a thing?
300.5(F) Backfill. Backfill that contains large rocks, paving materials, cinders, large or sharply angular substances, or corrosive material shall not be placed in an excavation where materials may damage raceways, cables, or other substructures or prevent adequate compaction of fill or contribute to corrosion of raceways, cables, or other substructures.
Where necessary to prevent physical damage to the raceway or cable, protection shall be provided in the form of granular or selected material, suitable running boards, suitable sleeves, or other approved means.