I searched a bunch of posts but came up empty handed. I would love to get some opinions...
What would you intrepret the burial depth of a 6-3 UF cable installed at a dwelling for a 120/240V, 50A circuit to power a sub panel in a detached shed.
Does column 1, row 1 apply?
Or, since its for dwelling related purposes, does column 1, row 6 apply (it's run through the middle of the yard and not under a driveway or parking area).
There seems to be some confusion here with an old timer at work who says 24" is it unless its under the drive/parking area...which at this house is dirt and some gravel but clearly identifiable from the yard.