300.5

Status
Not open for further replies.

Aselectric

Member
Location
New York
Occupation
Electrician
My question is in table 300.5 if I have a ridged metal conduit running under a roadway the table says 24” depth trench, but what if the roadway has 2” of concrete and then the roadway can I go 12” deep on my trench? Based on the 2nd location listed in table 300.5
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
No. You have to meet the most stringent condition. The "under a roadway" trumps the "covered" situation.
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
Also, the 24" is not the trench depth. Its is the cover (dirt) over the conduit. Your trench will be deeper than 24", depth will depend on the size of the conduit.
 

reast

Member
Location
Somerset, NJ
Occupation
Electrician
Agreed with the above. Table 300.15 for "Rigid metal conduit" says that you can reduce the depth if under concrete slabs of various thicknesses, but none of those situations apply if there is vehicular traffic, which you have. Therefore, the "below 2" concrete" doesn't apply because you have vehicular traffic, and the "Below a 4" concrete slab" doesn't apply because you have vehicular traffic and only a 2" slab. So go with the "under streets, roads...etc" section, which puts you at 24" of dirt, from the top of the dirt to the top of the conduit.
 